Table 2 Differences between positive and negative pressure rooms

From: Heating, ventilation and air conditioning (HVAC) in intensive care unit

Characteristic

Positive pressure system

Negative pressure system or airborne infection isolation room (AIIR)

Purpose

To create a protective environment to the patient to avoid acquiring any airborne infection (does not require an ante-room).

To create a protective environment to the healthcare providers as well as other patients in the ICU (requires an ante-room).

Type of patients requiring isolation

Burns, post-transplant, febrile neutropenia (also for patients in operating rooms)

Tuberculosis, swine flu, COVID-19 and other airborne viral diseases

Direction of airflow

Outside the room (away from the patients)

Inside the room (towards the patient)

Pressure

More than 2.5 Pa preferably + 8 Pa (ideal)

Less than 2.5 Pa

Supply air

More than the sum of return and exhaust air

Less than the sum of return and exhaust air

Recirculation

90–95%

80–90% (if required)

Air change per hour

> 20

≥ 12

Filtration efficiency

Supply: 99.97% at 0.3 μm DOP

All supply air must pass through HEPA filters

Supply: 90% (dust spot test)

All supply air to be exhausted without recirculation

HEPA (99.97% at 0.3 μm DOP) must be used on the supply side if recirculation is used.

HEPA is required on the exhaust side too, when exhausting air to the outside is not practical

  1. DOP dioctylphthalate particles of 0.3 μm diameter, Pa Pascal, HEPA high-efficiency particulate air filter, COVID-19 coronavirus disease 2019